Dépannage variables panelview 1000  RESOLU

Forum traitant des automates industriels de marque Allen Bradley et Rockwell
yvanwanji
Apprend le binaire
Apprend le binaire
Messages : 2
Inscription : 22 juil. 2022, 13:19

Dépannage variables panelview 1000

Message par yvanwanji »

Hello

I have to troubleshoot a panelview 1000 which communicates with a PLC5-20 controller via the DH+ protocol.
The problem is that at the level of the panelview 1000 all the memory variables are not read correctly, some are good and others display the ***********. My troubleshooting consists of displaying the data at the level of the variables that display the ************.

thank you for understanding
philou77
Mi homme - Mi automate
Mi homme - Mi automate
Messages : 2076
Inscription : 21 oct. 2015, 10:00
Localisation : Ile de France

Re: Dépannage variables panelview 1000  RESOLU

Message par philou77 »

Hi,

for many panels **** displayed instead of data equal to overflow

Change the paramter for displayed data :
Type (or amount of digit on left and right)

if your wrong data are Double type, an other cause is the inversion of Low and high word !
see parameters of the panel for that..
Si vous avez compris tout ce que je viens d'écrire, c'est que j'ai dû faire une erreur quelque part ! :D
yvanwanji
Apprend le binaire
Apprend le binaire
Messages : 2
Inscription : 22 juil. 2022, 13:19

Re: Dépannage variables panelview 1000

Message par yvanwanji »

Merci beaucoup