Hello
I have to troubleshoot a panelview 1000 which communicates with a PLC5-20 controller via the DH+ protocol.
The problem is that at the level of the panelview 1000 all the memory variables are not read correctly, some are good and others display the ***********. My troubleshooting consists of displaying the data at the level of the variables that display the ************.
thank you for understanding
Dépannage variables panelview 1000
-
- Mi homme - Mi automate
- Messages : 2084
- Enregistré le : 21 oct. 2015, 10:00
- Localisation : Ile de France
Re: Dépannage variables panelview 1000
Hi,
for many panels **** displayed instead of data equal to overflow
Change the paramter for displayed data :
Type (or amount of digit on left and right)
if your wrong data are Double type, an other cause is the inversion of Low and high word !
see parameters of the panel for that..
for many panels **** displayed instead of data equal to overflow
Change the paramter for displayed data :
Type (or amount of digit on left and right)
if your wrong data are Double type, an other cause is the inversion of Low and high word !
see parameters of the panel for that..
Si vous avez compris tout ce que je viens d'écrire, c'est que j'ai dû faire une erreur quelque part !
Re: Dépannage variables panelview 1000
Merci beaucoup